Dmitri S
Structural
- Jul 15, 2020
- 1
Hello everyone, hoping to get some input from you on an issue I have. I am a glazing contractor in NYC and I was hired to install several insulating units that compose of ~1/2 outer layer (two layers of 1/4 tempered glass with .060 pvb interlayer) with 1/2" air space over 3/8 tempered glass inner layer. The units are being structurally glazed on all four sides into curtainwall frame.
The issue is largest unit is roughly 193" wide by 105" tall. My engineer did the calculations on it and determined that it will deflect by 1.6" per NYC code calling for 30psf. He is stating that to his understanding any deflection should conform to table 1604.3 of NYC BC, which limits deflection to L/(120x0.7=84) or 3/4" which ever is less. He is willing to accept 1" as maximum.
However the design engineer that designed the project is arguing that the glazed wall is not a structural element, but rather "infill glazing" and therefore the code does not apply to it. He is stating that it is safe to design glass with deflection well exceeding 1". He is also requesting for wind load calculations per ASCE-7, which is 23.9PSF vs 30 per NYC code. My engineer says that NYC code must prevail.
The bottom line is it seems that there really is no specific reference to allowable glass deflection anywhere in the code, and it comes down to the engineer's discretion. Both engineers are very accredited and well respected in the industry, but I am stuck between a rock and a hard place. I will much appreciate any input that can help me move on with this project. I certainly do not want to install this glass in bad faith, and risk potential liability if it breaks and someone gets hurt.
P.S. Another concern that I have, is it possible that two panes of glass will deflect and touch in the middle since there is only 1/2" of air space separating them? My engineer says that it is impossible and they should always deflect in the same direction, but I am worried about positive air pressure inside the building putting pressure on the inner lite vs a gust of wind on the outside pushing on the outer lite - if they touch in the middle that can certainly cause one or both layers to break.
The issue is largest unit is roughly 193" wide by 105" tall. My engineer did the calculations on it and determined that it will deflect by 1.6" per NYC code calling for 30psf. He is stating that to his understanding any deflection should conform to table 1604.3 of NYC BC, which limits deflection to L/(120x0.7=84) or 3/4" which ever is less. He is willing to accept 1" as maximum.
However the design engineer that designed the project is arguing that the glazed wall is not a structural element, but rather "infill glazing" and therefore the code does not apply to it. He is stating that it is safe to design glass with deflection well exceeding 1". He is also requesting for wind load calculations per ASCE-7, which is 23.9PSF vs 30 per NYC code. My engineer says that NYC code must prevail.
The bottom line is it seems that there really is no specific reference to allowable glass deflection anywhere in the code, and it comes down to the engineer's discretion. Both engineers are very accredited and well respected in the industry, but I am stuck between a rock and a hard place. I will much appreciate any input that can help me move on with this project. I certainly do not want to install this glass in bad faith, and risk potential liability if it breaks and someone gets hurt.
P.S. Another concern that I have, is it possible that two panes of glass will deflect and touch in the middle since there is only 1/2" of air space separating them? My engineer says that it is impossible and they should always deflect in the same direction, but I am worried about positive air pressure inside the building putting pressure on the inner lite vs a gust of wind on the outside pushing on the outer lite - if they touch in the middle that can certainly cause one or both layers to break.