SteelPE
Structural
- Mar 9, 2006
- 2,743
I have gotten into a debate with a colleague recently. He mostly works on residential projects, I mostly work on commercial projects.
With regards to soil bearing, I am typically provided with a geotechnical report, however, when I am not, I typically look at table 1806.2 of IBC 2015. He typically has to reference table R401.4.1 of the IRC. Our debate centers around deck footings. He likes to use sonotubes with no base (12", 16", 18") I insist on using an enlarged base at the bottom of the footing, typically something called a Bigfoot. His argument is that the load are usually small, and if you are using a 18" dia sonotube, with an allowable soil bearing pressure in accordance with table R401.4.1 then the capacity of the pier is 5,300 lbs.
My beef with this method revolves around every soils report I have ever read has the following statement (or something very similar):
"The soil bearing capacity is based on a minimum footing width of 3' and must be reduced proportionately for narrower footings. Footings should be designed in accordance with SBC section 1806. For footings smaller than 3 feet in least lateral dimension, the allowable bearing pressure should be reduced to one-third of the above value multiplied by the least lateral footing dimension in feet. Also, we recommend that continuous wall footings be at least 18" wide and isolated footings at least 24" wide."
We are not talking large allowable bearing pressures in the case of the given soils report (typically 3,000-4,000 psf sometimes more).
I can't seem to find any minimum footing with in the IBC or IRC, however, every geotechnical report gives the same outline of parameters. So the question is:
-Are there any provisions in the IBC or IRC to reduce bearing capacity for footing size?
-If there are not provisions, would you use the full bearing capacities as outlined in table 1806.2 of the IBC or R401.4.1 of the IRC?
With regards to soil bearing, I am typically provided with a geotechnical report, however, when I am not, I typically look at table 1806.2 of IBC 2015. He typically has to reference table R401.4.1 of the IRC. Our debate centers around deck footings. He likes to use sonotubes with no base (12", 16", 18") I insist on using an enlarged base at the bottom of the footing, typically something called a Bigfoot. His argument is that the load are usually small, and if you are using a 18" dia sonotube, with an allowable soil bearing pressure in accordance with table R401.4.1 then the capacity of the pier is 5,300 lbs.
My beef with this method revolves around every soils report I have ever read has the following statement (or something very similar):
"The soil bearing capacity is based on a minimum footing width of 3' and must be reduced proportionately for narrower footings. Footings should be designed in accordance with SBC section 1806. For footings smaller than 3 feet in least lateral dimension, the allowable bearing pressure should be reduced to one-third of the above value multiplied by the least lateral footing dimension in feet. Also, we recommend that continuous wall footings be at least 18" wide and isolated footings at least 24" wide."
We are not talking large allowable bearing pressures in the case of the given soils report (typically 3,000-4,000 psf sometimes more).
I can't seem to find any minimum footing with in the IBC or IRC, however, every geotechnical report gives the same outline of parameters. So the question is:
-Are there any provisions in the IBC or IRC to reduce bearing capacity for footing size?
-If there are not provisions, would you use the full bearing capacities as outlined in table 1806.2 of the IBC or R401.4.1 of the IRC?