Hi all,
I've got a question regarding load factors. Say I am designing a free standing sign for wind forces and my governing overturning load combo is 0.6D + 1.0W per ASCE 7-05 ASD. I plan on using concrete blocks to resist any wind loads. To determine the amount of overturning force I must resist I factor the DL of the sign assembly and the WL per the above load combo. This would give me a required load to resist and I would place that amount of concrete block to resist (ignoring the DL reduction to the block and treating it as an "anchor").
Now lets say I have a client that uses strength design for load combo's. I would follow the same procedure except using 0.9D + 1.6WL. But, since I have a fixed block weight it would require roughly 60% more block. Unlike material design I don't get an "increase" in weight by using it's "ultimate strength".
I've always seen Strength Design and Allowable Stress as being approximately equivalent. Would I be out of line if I were to bring the required loads back to ASD levels when determining the amount of block needed?
I've got a question regarding load factors. Say I am designing a free standing sign for wind forces and my governing overturning load combo is 0.6D + 1.0W per ASCE 7-05 ASD. I plan on using concrete blocks to resist any wind loads. To determine the amount of overturning force I must resist I factor the DL of the sign assembly and the WL per the above load combo. This would give me a required load to resist and I would place that amount of concrete block to resist (ignoring the DL reduction to the block and treating it as an "anchor").
Now lets say I have a client that uses strength design for load combo's. I would follow the same procedure except using 0.9D + 1.6WL. But, since I have a fixed block weight it would require roughly 60% more block. Unlike material design I don't get an "increase" in weight by using it's "ultimate strength".
I've always seen Strength Design and Allowable Stress as being approximately equivalent. Would I be out of line if I were to bring the required loads back to ASD levels when determining the amount of block needed?