- Jul 29, 2013
- 133
I'm somewhat new to PT design, and have a question about service stresses. We use an FEM program to do final calculations (after performing preliminary calcs by hand). I often find that we will end up with a design section or 2 that exceed permissible stresses, just slightly. Our typical condition is a 2-way slab, where the limit is 6*sqrt f'c in tension (per ACI 318-11, 18.3.3).
In some cases, we are only exceeding the limit by ~5% (IE our allowable might be 464 psi, but we have a section at 488 psi), although sometimes is it more - up to 15% or so.
1) Do you ever ignore these over-stresses? Is there a limit under which you would consider it more of a local anomaly?
2) What would be the practical issue associated with exceeding the allowable stress? I assume cracking of the slab and potential re-distribution of moments, but if the slab has adequate strength isn't this just a serviceability issue?
3) I have found that adding tendons does not often help this issue significantly. I have to add a group of 3-4 tendons to have even a small impact. From a design standpoint, how do you typically make adjustments to get the slab stresses back within limits?
In some cases, we are only exceeding the limit by ~5% (IE our allowable might be 464 psi, but we have a section at 488 psi), although sometimes is it more - up to 15% or so.
1) Do you ever ignore these over-stresses? Is there a limit under which you would consider it more of a local anomaly?
2) What would be the practical issue associated with exceeding the allowable stress? I assume cracking of the slab and potential re-distribution of moments, but if the slab has adequate strength isn't this just a serviceability issue?
3) I have found that adding tendons does not often help this issue significantly. I have to add a group of 3-4 tendons to have even a small impact. From a design standpoint, how do you typically make adjustments to get the slab stresses back within limits?