Hello, this is a trivial, age old question, but I just want to confirm that HVAC COOLING equipment should be oversized due to altitude? Trane TRACE does not seem to oversize cooling coils due to altitude. Obviously it requires a higher CFM of airflow to deliver the same amount of heating/cooling. I may have to manually mark up a Trane Trace report because Trace does not automatically upsize the cooling coil.
This seems like an obvious answer, but I recently stumbled on this below article, and have heard varying answers. Maybe the logic behind not needing oversized cooling at altitude is that the cooling LOADS
(sensible and latent) are also derated and thus it offsets the cooling supplied. However, that wouldn't make sense because the same logic would apply to heating.
For heating with gas, there should be (2) derates correct? The gas heat output and the heat exchanger less dense air.
Thanks for any feedback