RHTPE
Structural
- Jun 11, 2008
- 702
I was reviewing a construction issue with a contractor this morning. He constructed a cast-in-place (CIP) retaining wall - nominally 20" thick with form liner on both faces, approximately 4" relief on the liner, reinforcing was based on the "core" 12 inch wall, 2" cover on rebar, resulting in 8" out-to-out of rebar. The original architectural detail for the railing posts called for embedded sleeves that would permit the posts to be grouted-in after the wall was complete. There was no additional rebar called for to surround the sleeves.
Needless to say, the embedded sleeves were left out. The rail installer core-drilled 4" diameter overlapping holes (2" c/c). The architect changed the posts from the original round to 2" x 4" rectangular. The aluminum posts were painted to avoid aluminum-to-concrete contact. The posts were set in the core-drilling holes and grouted.
Several months after the installation was complete, the wall cap cracked at each post, both sides, perpendicular to the wall face. In fact, the posts at the ends of the wall completely spalled off the cap.
I suspect that the grout used was either non-shrink or an anchoring grout (trade name avoided) that has an expansive property. Most non-shrink grouts exhibit a +4% volume change early on, shrinking back to about a 0% to +0.3% change at full cure. Had the embedded sleeves been used the slightly expansive nature of a grout would have been better contained and perhaps had less of an impact on the wall's cap. I do not suspect that a reaction between the aluminum posts and the grout caused an expansive corrosion product.
Anyone care to chime in? Can a petrographic analysis of the grout used determine its expansive nature?
Ralph
Needless to say, the embedded sleeves were left out. The rail installer core-drilled 4" diameter overlapping holes (2" c/c). The architect changed the posts from the original round to 2" x 4" rectangular. The aluminum posts were painted to avoid aluminum-to-concrete contact. The posts were set in the core-drilling holes and grouted.
Several months after the installation was complete, the wall cap cracked at each post, both sides, perpendicular to the wall face. In fact, the posts at the ends of the wall completely spalled off the cap.
I suspect that the grout used was either non-shrink or an anchoring grout (trade name avoided) that has an expansive property. Most non-shrink grouts exhibit a +4% volume change early on, shrinking back to about a 0% to +0.3% change at full cure. Had the embedded sleeves been used the slightly expansive nature of a grout would have been better contained and perhaps had less of an impact on the wall's cap. I do not suspect that a reaction between the aluminum posts and the grout caused an expansive corrosion product.
Anyone care to chime in? Can a petrographic analysis of the grout used determine its expansive nature?
Ralph