I have a customer with a DI water system. The cold loop (ambient temp) keeps heating up during times of low usage (nights and weekends). I predicted this, but they thought it would be insignificant.
I need to add a cooler to the loop at some point and am working on sizing it. I have only three sources of heat as far as I can see; 2 hp centrifugal pump on ozonation loop + 10 hp centrif pump on main loop, and 3400 watts (4.4 hp) from a UV unit. I figure that WORSE case scenerio I am introducing 16.4 hp of energy to the water system. This would be if ALL the hp from the pumps is being converted into heat from line and impellar friction. I calculate that I should be oversized with a 3 ton refrigeration unit and an exchanger.
I have a salesman that seems to think that they need a 25 ton unit??? I am doubting my numbers a little bit?
Thanks
I need to add a cooler to the loop at some point and am working on sizing it. I have only three sources of heat as far as I can see; 2 hp centrifugal pump on ozonation loop + 10 hp centrif pump on main loop, and 3400 watts (4.4 hp) from a UV unit. I figure that WORSE case scenerio I am introducing 16.4 hp of energy to the water system. This would be if ALL the hp from the pumps is being converted into heat from line and impellar friction. I calculate that I should be oversized with a 3 ton refrigeration unit and an exchanger.
I have a salesman that seems to think that they need a 25 ton unit??? I am doubting my numbers a little bit?