American voltage level
6
Hi All,
I am invloving one project which which employ american voltage level. As far as I know, american has the following voltage type(60Hz):
120/208V for lighting and outlet, solid earthed
240/416V for ? solid earthed
277/480V for LV such as motor, solid earthed
2425/4200V for MV load, low resistance earthed
the Higher voltage ?
Could anyguys help me to confirm whether it is right and detail it? what type of consumer will use which voltage?
In general, what's standard transformer type?
thanks in advance
skogsgurra's story reminds me of a generator I saw at the Bonneville dam. On the side of this huge generator was a 15A 120V receptacle. Just seemed a little like overkill.
Think of the toaster that that would have run....
rmw
15A is 15A, but think of the fault current if the toaster shorted!
A 15A receptacle fed through a 45kVA (a guess) step down transformer really isn't going to have much more fault current behind it at Bonneville than it would much further down the power system.
So, where was the ;-)?
I figured you ought to know that, but who know about some of the readers that might stumble across that.
[cheers]
In my area a typical, modern, non-manufacturing facility would have a MV service at 13.2 KV this would be transformed at the main service to 480/277 volt 3phase 5 wire. This voltage is distributed to the electrical rooms where the panelboards supply the motors and large loads with 480 volt 3 ph. The panels also supply the 277 volt 1 ph.lighting loads with power that is derived from one leg of the 480 and the grounded neutral for the 277 volt.
At the main service the 13.2 KV also feeds a second transformer for the 208/120 loads such as the wall receptacles and other loads such as VAV boxes on the A/C system. All transformers are Delta primary/Wye secondary with the neutral grounded. Manufacturing facilities, old buildings, and residences use some of the other voltages and configurations mentioned elsewhere. Hope this helps.