Bill3752
Chemical
- Jan 24, 2008
- 135
I am evaluating the storage unit of a large Ammonia plant. This unit has installed a bunch of Rego thermal relief valves. While the relief case is indeed thermal, these valves are not ASME certified.
Per API 520 "Before the ASME Code incorporated requirements for capacity certification, valves were generally sized for liquid service .... This method assumes an effective Kd = .62 and 25% overpressure. An additional factor, Kp, is needed for relieving pressures other than 25% {.6 for 10% ovp case}. This sizing method may be used where capacity certification is not required or was never established."
My question relates to the "or was never established". I am thinking that I can used the non-certified valves, but the capacity must reflect the .6 factor.
Has anyone run into this, and is my thinking correct - i.e. it is ok to used non-certified valves in ASME service, assuming they pass after de-rating their capacity?
Per API 520 "Before the ASME Code incorporated requirements for capacity certification, valves were generally sized for liquid service .... This method assumes an effective Kd = .62 and 25% overpressure. An additional factor, Kp, is needed for relieving pressures other than 25% {.6 for 10% ovp case}. This sizing method may be used where capacity certification is not required or was never established."
My question relates to the "or was never established". I am thinking that I can used the non-certified valves, but the capacity must reflect the .6 factor.
Has anyone run into this, and is my thinking correct - i.e. it is ok to used non-certified valves in ASME service, assuming they pass after de-rating their capacity?