Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Analog for Allen-Bradley Rockwell

Status
Not open for further replies.

occupa

Electrical
Dec 16, 2009
2
I am looking for a third party supplier that can provide an analog module with higher resolution than 16/15 bit currently available in the A-B product line.

I this is not available would I be able to find this type of input sensitivity in another brand Siemens, Automation Direct etc.

 
Replies continue below

Recommended for you

Analog in/out of ab contrologix is this
4-byte floating-point number -3.402823E38 to -1.1754944E-38

Maybe your talking PLC5 or slc500? Which is legacy products.


 
Thanks for the input I looked up the specifications on a 1756-IF8 and the Input Range and Resolution is 15/16 bit.

You are correct the data format is Floating point IEEE 32 bit.

I am looking for a converter with greater than 16 bit Range and Resolution specs.

I am guessing this would have to be from a third party supplier.
 
What you get on analog input resolution is based on the type of A/D converter used and is always a compromise between speed, noise immunity, resolution and cost. PLCs tend to go for the middle ground, partly because PLC system design is generally optimized for fast sequential logic solving, so adding something slower but with higher resolution is going to potentially bog down the primary mission of the device. DCS systems on the other hand use much more powerful processors so they can deal with the higher resolution inputs (i.e. up to 24 bit). But that capability comes at substantially higher cost as a control system, hence their primary mission being plant wide process controls, not machine controls. PLCs have been used for plant wide control systems and SCADA systems, but not typically when high analog resolution is a necessity. Jut like in horse racing, you have to know your horse before you put your money on it.

As my old mentor first told me when I asked about the difference between a DCS and a PLC, he said "PLCs make things, quickly; DCS systems make stuff, accurately."

All that said, Siemens uses their S7-400 PLC I/O hardware for their PCS-7 DCS system, and because of that, they have Analog cards with 24 bit resolution A/D converters (although you only can use 20 bits + sign I think). Of course, that is their most expensive PLC system as well. I think the S7-300 has higher than 16 bit A/d converters but you only can use up to 16 bit on some types of signals.

Have you considered using a separate stand-alone PID controller with higher resolution for direct control of that process and then extracting only pertinent data from is for use in the PLC program?

"Dear future generations: Please accept our apologies. We were rolling drunk on petroleum."
— Kilgore Trout (via Kurt Vonnegut)

For the best use of Eng-Tips, please click here -> faq731-376
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor