I have been asked to verify the structural stability for a 40-year-old bar joist in the Miami area. I am analyzing the roof joist using a computer model based on measurements taken in the field. The bottom chord is a double bar (3/4” dia each), the 28”-9” long top cord is a 2L 2x2x1/4, and the webs are solid 7/8” dia. bars. Per field observations there are three rows of cross bridging, which seems alrigth for this span length. I have assumed that all joints are pined and that the two end supports in the joist are fixed. I am using Fy=36 ksi (I am not very sure about that Fy yet).
After applying all the loading the bottom chord fails in compression due to wind uplift. I took the compression force and run manual calcs to determine the unsupported length which gives me about 47 inches. The max compression force is about 6.2 kips.
I am inclined to suggest they provide additional bridging at 4.5 feet o.c. (the bar joist ‘bays’ are 1.5 feet wide. I am assuming there is some fixity at the points where the bridging connects to the joist then I could apply K=0.8)
My question is: Does the bridging effectively restrain the bottom chord so that the KL=0.8 x 4.5’ is satisfactory?. Shouldn’t I use K=0.8?
Any input will be greatly appreciated.
After applying all the loading the bottom chord fails in compression due to wind uplift. I took the compression force and run manual calcs to determine the unsupported length which gives me about 47 inches. The max compression force is about 6.2 kips.
I am inclined to suggest they provide additional bridging at 4.5 feet o.c. (the bar joist ‘bays’ are 1.5 feet wide. I am assuming there is some fixity at the points where the bridging connects to the joist then I could apply K=0.8)
My question is: Does the bridging effectively restrain the bottom chord so that the KL=0.8 x 4.5’ is satisfactory?. Shouldn’t I use K=0.8?
Any input will be greatly appreciated.