I'm trying to check the work of my structural engineer. He's got 5/8" anchor bolts spaced at 8"OC attaching a sill plate to the top of a basement 6" ICF wall. Joists hang off the sill plate. 1-1/8" floor sheathing attaches to the top of the sill plate with 2 rows of #8 screws 4"OC. Say's it's necessary to restrain the top edge of the wall. I've NEVER seen spacing at 8" for an anchor bolt. This structure isn't particularly unusual (other than I think it's a bit weird to hang the joists from the sill plate rather than on a ledger board.)... 8' ceiling basement. 7.5' unbalanced backfill behind the wall.
So here's the big question I don't understand. Given the spacing there are 4 #8 screws attaching the plywood to the sill plate for every 5/8" anchor bolt. If we look at the cross section of the associated fasteners, the 5/8" bolt has a shear area of 0.218in^2. The four #8 screws have a shear area of 0.039in^2 COMBINED. And that assumes the screws shear before they pullout. It would seem we have nearly an order of magnitude discrepancy here.
So here's the big question I don't understand. Given the spacing there are 4 #8 screws attaching the plywood to the sill plate for every 5/8" anchor bolt. If we look at the cross section of the associated fasteners, the 5/8" bolt has a shear area of 0.218in^2. The four #8 screws have a shear area of 0.039in^2 COMBINED. And that assumes the screws shear before they pullout. It would seem we have nearly an order of magnitude discrepancy here.