I have recently waded thru all the formulae in ACI 318-2002 Appendix D for computing anchor bolt capacities! IBC 2000 Section 1913 is similar.
It seems to me that everything is based upon capacities in unreinforced concrete.
When anchor bolts, subjected to shear, are embedded in a reinforced concrete pier, it would seem that the ties will work like stirrups to resist the shear if they are spaced at d/2. The d/2 requirement is closer tie spacing than normally required for piers. The compressive force in the pier (if there is any)will obviously increase the shear capacity. To prove that the anchor bolts are OK in shear, it seems logical to check the allowable shear of the reinforced pier instead of the breakout strength of the anchors in the unreinforced concrete. Steel strength and pryout strength of the anchors also need to be checked.
When anchor bolts, subjected to tension, are embedded in a reinforced concrete pier, it would seem that the overlap of the anchor bolts and the reinforcing steel has to be long enough to transfer the tensile forces. To prove that the anchor bolts are OK in tension, it seems logical to check the tension that can be transfered to the reinforcing instead of the breakout strength of the anchors in the unreinforced concrete. Of course, the steel strength of the anchors also need to be checked.
I would then use the minimum values of the capcities in the combined stress equations.
For anchors in footings, I use the formulae in the code for anchors in unreinforced concrete.
Is this how others are currently doing it or are you relying on old tables like I used to? You need a major spreadsheet to handle these new calculations. Pretty involved process.
Any comments?
It seems to me that everything is based upon capacities in unreinforced concrete.
When anchor bolts, subjected to shear, are embedded in a reinforced concrete pier, it would seem that the ties will work like stirrups to resist the shear if they are spaced at d/2. The d/2 requirement is closer tie spacing than normally required for piers. The compressive force in the pier (if there is any)will obviously increase the shear capacity. To prove that the anchor bolts are OK in shear, it seems logical to check the allowable shear of the reinforced pier instead of the breakout strength of the anchors in the unreinforced concrete. Steel strength and pryout strength of the anchors also need to be checked.
When anchor bolts, subjected to tension, are embedded in a reinforced concrete pier, it would seem that the overlap of the anchor bolts and the reinforcing steel has to be long enough to transfer the tensile forces. To prove that the anchor bolts are OK in tension, it seems logical to check the tension that can be transfered to the reinforcing instead of the breakout strength of the anchors in the unreinforced concrete. Of course, the steel strength of the anchors also need to be checked.
I would then use the minimum values of the capcities in the combined stress equations.
For anchors in footings, I use the formulae in the code for anchors in unreinforced concrete.
Is this how others are currently doing it or are you relying on old tables like I used to? You need a major spreadsheet to handle these new calculations. Pretty involved process.
Any comments?