CN-EIT
Structural
- Feb 10, 2020
- 31
Context: Baseplate at a braced frame transferring shear to anchor rods; that is, no frictional shear transfer. Anchor rod layout is square consisting of 3/4" diameter anchor rods in 1 5/16" holes w/ 2" plate washer (not welded to baseplate)
Discussion:
1) AISC DG-1 recommends that only two anchors be used to resist the shear; subsequently, concrete failure mechanisms are calculated assuming only 2 anchors are utilized to resist shear.
2) DG-1 goes on to say that if 4 anchors are to be utilized, it is recommended that a plate washer with internal diameter 1/16" greater than the anchor bolt diameter be used and welded to the baseplate.
2a) If one were to weld a washer to the baseplate, my presumption is that it limits your slip before engaging four anchors to 1/16" of an inch. It does not expound upon sizing the weld; my presumption is the weld would need to be designed such that the weld strength is sufficient to carry the full shear from baseplate to anchor rod.
3) To my knowledge, there is no code provision saying that unless you weld a plate washer to the baseplate, you can only use two anchor bolts in resisting shear.
Example for Reference: 10"x10"xthickness baseplate with 4 3/4" diameter anchor rods in 1 5/16" holes. Assuming no welded washers, if all anchor bolts were perfectly placed, the slip before engaging all four anchors would be 5/16". In the worst case scenario, the slip would have to be 9/16" but the baseplate where it bears against the anchor rods would need to yield or tear.
Question 1: Can a valid argument be made to distribute shear to 4 anchor rods without welding plate washers?
Question 1a: Say the baseplate is dropped below finished floor elevation and subsequently encased in concrete. The concrete is not monolithic to the pier or the adjacent slab on grade (column isolation joint), however, can an argument be made that this provides a degree of confinement sufficient to distribute the shear force to all anchors?
Discussion:
1) AISC DG-1 recommends that only two anchors be used to resist the shear; subsequently, concrete failure mechanisms are calculated assuming only 2 anchors are utilized to resist shear.
2) DG-1 goes on to say that if 4 anchors are to be utilized, it is recommended that a plate washer with internal diameter 1/16" greater than the anchor bolt diameter be used and welded to the baseplate.
2a) If one were to weld a washer to the baseplate, my presumption is that it limits your slip before engaging four anchors to 1/16" of an inch. It does not expound upon sizing the weld; my presumption is the weld would need to be designed such that the weld strength is sufficient to carry the full shear from baseplate to anchor rod.
3) To my knowledge, there is no code provision saying that unless you weld a plate washer to the baseplate, you can only use two anchor bolts in resisting shear.
Example for Reference: 10"x10"xthickness baseplate with 4 3/4" diameter anchor rods in 1 5/16" holes. Assuming no welded washers, if all anchor bolts were perfectly placed, the slip before engaging all four anchors would be 5/16". In the worst case scenario, the slip would have to be 9/16" but the baseplate where it bears against the anchor rods would need to yield or tear.
Question 1: Can a valid argument be made to distribute shear to 4 anchor rods without welding plate washers?
Question 1a: Say the baseplate is dropped below finished floor elevation and subsequently encased in concrete. The concrete is not monolithic to the pier or the adjacent slab on grade (column isolation joint), however, can an argument be made that this provides a degree of confinement sufficient to distribute the shear force to all anchors?