PostFrameSE
Structural
- Sep 5, 2007
- 174
Is it possible to connect to the face of the top course of a CMU wall (designed as a bond beam or lintel with horizontal reinforcing and vertical reinforcing punching through the cores to tie down to foundation) in lieu of depending on precise placement of anchor bolts by blocklayers such that I don't have to be quite so concerned about precise anchor bolt placement? I work with wood trusses spaced approximately 8' o.c. and the uplift loads can be on the order of 2-3kips, and therefore, anchor bolt placement is critical. Will anchoring to the face create a "block shear" or tension failure in the block itself, or can a "scoop-block" be counted on to carry the shear loads (vertical uplift) adequately? Any direction would be appreciated. Thanks.