Hello all,

I looked at a modular foundation that is built like most are.....dry stacked piers. Is this specifically ruled out as an option from the FHA/HUD permanet foundation manual even if there are other lateral support systems such as X bracing and/or straps? Thanks!
 
Replies continue below

Recommended for you

Hi TimmyH76,

Section 503-4 (MASONRY PIERS AND WALLS) of the FHA/HUD Guidelines has the following: "All masonry piers and walls shall have mortared bed and head joints. Reinforcing and grouting shall be in accordance with the foundation concept selected from Appendix A and designed in Appendix C."

I found a website that said the only HUD/FHA approved retrofit for "dry stack" masonry piers is outlined in HUD's material release 907 F (see link below):


Also, a document you might want to take a look at is "Guide to Foundation and Support Systems for Manufactured Homes," which can be found on the website:


Hope this helps :)
 
One more note: in the foundations guide I found on the website (the second link in my previous post), two of their case studies (#2 and #8) specifically mention that dry stacked piers are used... So why would they mention that if it was not allowed? I'm not sure, maybe somebody else can weigh in on this.
 
In some cases, dry stacked are used if an approved surface bonding product/material (skim coat of cement, sand, bonding materials and fibers) is used to increase the shear and tensile strength of the dry stacked masonry.

Dick
 