We are developing a bus bar for a utility customer that wants a C119.6 certification. The test spec they require involves 500 four-hour current cycles at 950 amps, 2 hours on followed by 2 hours off. Resistance is measured in micro Ohms and once a baseline resistance for the bar assembly (bar, receivers, set screws) is established, the bar must remain within 5% of that value throughout the test, as measured in micro Ohms. All of the bar components are CNC milled aluminum, 6061 and 2024.
We have gone through the test twice now. In each case one bar (out of four tested each time) has dropped outside the 5% micro-Ohm range, i.e. with an out of bounds low resistance. In each case the resistance has subsequently increased through the cycling to return to the acceptable range.
We are wondering if there is anything we can do to make it more likely that we get the test result our customer requires. We are assembling the bar 'dry' without conductive grease. Could a conductive grease help, or would it just make the situation worse? Any other wisdom we should apply to get 'er done?
best,
Brandt
We have gone through the test twice now. In each case one bar (out of four tested each time) has dropped outside the 5% micro-Ohm range, i.e. with an out of bounds low resistance. In each case the resistance has subsequently increased through the cycling to return to the acceptable range.
We are wondering if there is anything we can do to make it more likely that we get the test result our customer requires. We are assembling the bar 'dry' without conductive grease. Could a conductive grease help, or would it just make the situation worse? Any other wisdom we should apply to get 'er done?