HuskyFC450
Mechanical
- Oct 12, 2012
- 8
The manufacturing facility where I am employed as an electrician has never had an "Electrical Hazard Assessment, Arc Flash Analysis/Survey, or any ANSI/NETA MTS tesing performed on any of it's electrical distribution or protective relay equipment. Most (if not all) of the electrical equipment and Molded Case CB's have been in place for 25 years without even being exercised. There has never been an Electrical Maintenance Program since this company was first formed. I have been adamant in my pursuit to have the company bring in a NETA-certifed contractor to perform verification tests on all of the OCPD's, but they seem to be taking the stance of "well, we,ve never needed this before...why now?" One of my concerns is this: They have contacted their insurance group to find an EE(PE) that has experience with Arc Flash Analysis and Surveys. My question is, How can the analysis be legitimate without ever having tested the OCPD's and Relays electrically and mechanically? It's widely an accepted fact within industry that MCB's over 5-years of service will fail to operate correctly 15% of the time, or operate at a much slower speed the first time they are tripped. This significantly increases the incident energy exposure in an Arc Flash scenario. Is this common industry practice to have an Arc Flash Survey performed without ever testing the equipment? Can a company be NFPA-70E compliant without EVER having NETA-certified testing of said electrical equipment?