mcm00048
Electrical
- Aug 31, 2017
- 21
Good Morning all,
I am working now in a Grid Connected PV Project located in Spain. In the MV Switchgear Arrrangement, it is requested to provide space anti condensation heaters to avoid condensation. Such heaters shall be fed from an auxiliary power supply of 230 Vac or 125 V ac
During night, there is no power available from Inverters. In those cases, from which power supply the Space heaters are fed?, I guess it is made by the external grid supply. But, it comes to my mind the following question. In case of shutdown of the plant and also Grid is not available for feeding the loads of the Plant ( Heaters in this case) due to maintenance or replacement of Step-Up Transformer, what could be the power supply for these electrical loads? Here below:
1. Diesel Generator System , feasible?
2. Oversizing of battery rack
3. Shutdown of all equipment including heaters could cause malfunctioning or failure of MV Switchgear?
Thank you in advance,
In addition to above, I would like you to tell me names of books / literature of operation related with PV Plant operation, commisioning, scheduled shutdowns as well as emergency operation of this PV Plants It would be appreciated!
Hope all of you have a nice week,
Miguel.
I am working now in a Grid Connected PV Project located in Spain. In the MV Switchgear Arrrangement, it is requested to provide space anti condensation heaters to avoid condensation. Such heaters shall be fed from an auxiliary power supply of 230 Vac or 125 V ac
During night, there is no power available from Inverters. In those cases, from which power supply the Space heaters are fed?, I guess it is made by the external grid supply. But, it comes to my mind the following question. In case of shutdown of the plant and also Grid is not available for feeding the loads of the Plant ( Heaters in this case) due to maintenance or replacement of Step-Up Transformer, what could be the power supply for these electrical loads? Here below:
1. Diesel Generator System , feasible?
2. Oversizing of battery rack
3. Shutdown of all equipment including heaters could cause malfunctioning or failure of MV Switchgear?
Thank you in advance,
In addition to above, I would like you to tell me names of books / literature of operation related with PV Plant operation, commisioning, scheduled shutdowns as well as emergency operation of this PV Plants It would be appreciated!
Hope all of you have a nice week,
Miguel.