Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations SSS148 on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Any good references for foundation deflection design?

Status
Not open for further replies.

camsmitt

Structural
Nov 20, 2005
2
I have a soils report which limits the deflection of the continuous footing to l/240. I have been given the criteria of vertical subgrade modulus of 100 lbs/sq in / in of deflection and 1,000 psf bearing. I have never been given the Subgrade modulus before, not sure of the application.
 
Replies continue below

Recommended for you

It sounds as if you have a poor soil with only 1000 psf bearing. The subgrade modulus simply tells you how much deformation you can expect. At 100 psi (14,400 psf) you could expect 1", so at 1000 psf you could expect 0.07".

BA
 