Waqalevu
Electrical
- Aug 8, 2014
- 18
We have an 400 Volt alternator driven by a CHP and connectect to an 11 KV busbar by way of a step up transformer. This setup has been working fine now for a few years. All of a sudden we are getting strange voltages indicated on the mains side side when the machine is at rest. When we run up the machine, we are getting voltage mis-match faults. The mains voltage is monitored between phases, and phase to earth and indicated at A on the diagram and displayed on the HMI. These voltage readings are when the generator is at rest and are unbalanced, ranging from about 370 Volts to 428 Volts, and absolutely silly voltages between phase and neutral. The only neutral we have is connected to the star point of the alternator. I think we are getting these strange readings, as we are measuring from the transformer phase to the generator neutral, so this may not be a bearing on the fault. We have found a couple of failed (open circuit) diodes on the exciter, and have replaced all twelve diodes, but the fault is still with us.
Appreciate if anyone can help on this as we have come to a dead end on what to check next. I am thinking that maybe the exciter has lost its magnetism. A drawing of the system is attached.
Appreciate if anyone can help on this as we have come to a dead end on what to check next. I am thinking that maybe the exciter has lost its magnetism. A drawing of the system is attached.