API 2000: Credit for depressuring device for N2 Pad Valve Failure

Status
Not open for further replies.

ChemenggEIT

Chemical
Sep 19, 2007
3
I am revalidating PVRV for API 620 LP Tank. API 2000 doesn't say anything about credit for depressuring device for Inert Pad Failure. Can i take credit for flow through depressuring valve?

Thanks in advance for any feedback
 
Replies continue below

Recommended for you

Credit will only be taken when you can demonstrate that the depressuring loop is "absolutely reliable" e.g. SIL4...
 
i would consider the case you described as being double jeopardy unless for some reason you believe the two are linked. becuase it sounds like you might have a simple regulator in and a back pressure regulator out.

what is the likelihood of failure at the same time? and are the failures related?

is the depad device a simple back pressure regulator? or is a control valve with a control loop from a PIT?

is the pad regulator a pilot operated with remote sensing line that is also connected to a common valve that provides the tap to a PIT to a PIC? that could result in a common root cause failure that could impact both the supply and outlet, etc.

are you likely to be filling the tank and using the capacity of the depad regulator when you have the supply failure?

you need to define your credible scenarios and then address them.
 