AwesomeAndy3

Civil/Environmental
Jan 26, 2021
10
Hi everyone,

Does anyone have experience in completing API 2000 calculations?

I am just a little confused on what my next step would be.

I was able to calculate the normal inbreathing and outbreathing calculations for a tank I'm working on. (840.1Nm^3/hr for inbreathing and 431.2Nm^3/hr for outbreathing). Product is ethanol.

How am I supposed to work with this to ensure the tank will have adequate venting requirements? In other words, how do I calculate the quantity of roof vents and sizes I would need? Or how do I analyze the existing roof vents to make sure there are enough venting on the roof?

I apologize as I am quite new to this.

Thanks,
 
Replies continue below

Recommended for you

Vent manufacturers should be able to supply you a curve of flow vs pressure across the vent. That will help you choose the size and quantity.

Have you calculated the emergency venting requirement?
 
At some point, you need the design and operating pressures and vacuums for the tank.
And that coupled with the vent flow curves will give vent sizing or numbers.
Note that there are special provisions for tanks with internal floating roofs, special provisions for frangible roofs also.
If the tank is existing, or if no pressure/vacuum rating was specified, it may be more involved to come up with those pressure/vacuum ratings.
Also, be aware that pretty much each revision of API-650 has revised various requirements dealing with wind and pressure uplift and ratings.
 
If you search API 2000 on this site many posts will come up which will help you.

Be aware that the negative pressure of many API 650 tanks is very small ( 1 " WG) so this will probably be your critical sizing especially a sit is the biggest one.

As a ROT, you need the inlet vent area to be at least as big as the nozzle size of the exit pipe on the tank as a start point at least if this is a simple vented tank.

Are you sure you can freely vent ethanol?

Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 
Thanks everyone,

IFRs - I have yet to calculate the emergency venting requirement, will do it shortly. I assume an emergency vent is required to satisfy/meet the emergency venting requirement on its own? As opposed to adding all the other open vents to see if it exceeds the emergency venting requirements?

JStephen - This existing tank will be modified to include an internal floating roof (not a frangible roof), are the special provisions for internal floating roof just the fact that you need circulation vents across the fixed tank roof as per API 650 Section H.5.2.2.? I could check the vent flow curves from these circulation vents to make sure they exceed the requirement for inbreathing/outbreathing areas right?

LittleInch - Yea ethanol seems to have a pretty low flash point (12.7C). I believe I also need to calculate flash equilibrium equations? Since the operating temperature of the tank is -9C to 27C. To be honest I'm not sure how to perform equilibrium flash calculation to increase the out-breathing venting requirements. Also, what exactly is the inlet vent area? Are there differences on the roof nozzles in regards to inlet/outlet vent nozzles? I apologize for the lack of knowledge I have in regards to this.

Thanks again.
 
Your whole issue just went away because you are putting in an IFR which requires circulation vents. Put them in and toss API 2000. You don't need any other venting. You don't need flow curves for the circulation vents. Your day just got easier!!!
 
Listen to IFRS.

Circulation vents are HUGE compared to any other sort of vent so with an internal floating roof you are not looking at the same thing.

Same goes for the flash calcs - the floating roof prevents additional emissions.

I am though a little worried that you appear to be designing something which is clearly outside of your knowledge or experience, but is potentially very dangerous.

Do you not have other experienced personnel to discuss this with or check or approve your design??

Modifying tanks is not a simple exercise.



Remember - More details = better answers
Also: If you get a response it's polite to respond to it.
 