- Nov 9, 2021
- 28
Hi all,
I'm designing a diesel tank 14m Diameter, 15m high tank with a fixed roof (rafters and roof plate).
Max inlet flow rate = 870 m^3/h DN250
Max outlet flow rate = 440 m^3/h DN250
Tank is at atmospheric pressure
I'm a Structural Engineer and haven't had any exposure to the Venting requirements set out in API 650. I've calculated the in-breathing and out-breathing flow rates (I think)which are:
Outbreathing rate = 870 m^3/h
Inbreathing rate = 1470 m^3/h (thermal governs)
I've also calculated the emergency pressure vent flow capacity = 18362 Nm^3/h
On the client supplied data sheet they've nominated 3 x DN200 free vents on the roof (for us to confirm) and I'll need to nominate a diameter on the emergency pressure vent (which their standard drawing nominates a Protectoseal 53300.
2 questions:
a) what am I missing in order to calculate the diameter of the free vents required?
b) what am I missing in order to calculate the diameter of the emergency pressure vent? Is this diameter typically specified by the manufacturer or by the designer?
The company wasn't going to engage a mechanical engineer for this project, but I'm hesitant to nominate sizes for these as I feel it isn't really my domain.
Any help would be appreciated,
Thanks
I'm designing a diesel tank 14m Diameter, 15m high tank with a fixed roof (rafters and roof plate).
Max inlet flow rate = 870 m^3/h DN250
Max outlet flow rate = 440 m^3/h DN250
Tank is at atmospheric pressure
I'm a Structural Engineer and haven't had any exposure to the Venting requirements set out in API 650. I've calculated the in-breathing and out-breathing flow rates (I think)which are:
Outbreathing rate = 870 m^3/h
Inbreathing rate = 1470 m^3/h (thermal governs)
I've also calculated the emergency pressure vent flow capacity = 18362 Nm^3/h
On the client supplied data sheet they've nominated 3 x DN200 free vents on the roof (for us to confirm) and I'll need to nominate a diameter on the emergency pressure vent (which their standard drawing nominates a Protectoseal 53300.
2 questions:
a) what am I missing in order to calculate the diameter of the free vents required?
b) what am I missing in order to calculate the diameter of the emergency pressure vent? Is this diameter typically specified by the manufacturer or by the designer?
The company wasn't going to engage a mechanical engineer for this project, but I'm hesitant to nominate sizes for these as I feel it isn't really my domain.
Any help would be appreciated,