ird192
Civil/Environmental
- May 7, 2007
- 15
I have a client that has a above ground storage tank , a chemical spill damaged a area of the shell 10" wide 18' vert. the shell plate is three different thickness . My interpretation of Section 9 allows for removal of the damaged shell plate and 1 continuous insert plate to be welded back while meeting vert. spacing requirements in API 653 . The plate would cover 2 horizontal welds which si acceptable per this code . I dont see any issue with installing 1 continuous plates as long as it meeting the design requirements of API 650 , verus installing 3 spearte insert plates, comments are welcom , B hart API 653 / PE Thanks