- 44
Hi All,
Can anybody throw some light on clause 5.8 of API 6D 24th edition.
[highlight #F57900]"Valve cavity relief pressure when added to the valve pressure rating shall not exceed 133 % of the pressure rating of the valve at its maximum specified design temperature"[/highlight]
1) "when added" I am unable to exactly interpret this (though looks simple math ) How much shall be minimum and maximum cavity relief pressure exactly?
2) Valve pressure rating at what temperature?
3) What is meant by maximum specified design temperature? Is it manufacturer design temperature or purchaser specified design temperature?
4) This means cavity relief pressure will change with temperature?
Also,
Clause H.8 Cavity relief testing says
[highlight #F57900]"Failure to relieve at a pressure less than the valve cavity relief pressure per 5.8 shall be cause for rejection"[/highlight]
In above sentence "Less than" means I have to maintain "some pressure" in cavity all the time?
Cheers !!!
Can anybody throw some light on clause 5.8 of API 6D 24th edition.
[highlight #F57900]"Valve cavity relief pressure when added to the valve pressure rating shall not exceed 133 % of the pressure rating of the valve at its maximum specified design temperature"[/highlight]
1) "when added" I am unable to exactly interpret this (though looks simple math ) How much shall be minimum and maximum cavity relief pressure exactly?
2) Valve pressure rating at what temperature?
3) What is meant by maximum specified design temperature? Is it manufacturer design temperature or purchaser specified design temperature?
4) This means cavity relief pressure will change with temperature?
Also,
Clause H.8 Cavity relief testing says
[highlight #F57900]"Failure to relieve at a pressure less than the valve cavity relief pressure per 5.8 shall be cause for rejection"[/highlight]
In above sentence "Less than" means I have to maintain "some pressure" in cavity all the time?
Cheers !!!