Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

API RP 505 (hazardous area classification) Annex D

Status
Not open for further replies.

Guidoo

Chemical
Sep 13, 2002
266
API RP 505 for "Classification of Locations for Electrical Installations at Petroleum Facilities Classified as Class 1, Zone 0, Zone 1, and Zone 2" contains an Appendix D (Informative Annex) with an alternate method for area classification.

Radii as found using this alternate method can be quite different from the ones calculated using methods from chapters 8-10 of the Recommended Practice. Anyone having any idea why this appendix is there, an when it should be applied?
 
Replies continue below

Recommended for you

Based on API RP 505, the recommended ventilation for hazardous and non-hazardous areas is 12 and 6 ach respectively. From a Fugitive Emissions study I came up with only 2ach required for adequate ventilation. What flow rate I should apply? The recommended or the calculated?

Is that recommended ACH for the "whole room" or just the zone 1 area limited by the extensions suggested by API RP 505?

Please help... :-/

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor