API STANDARD 661

Status
Not open for further replies.

mafla jones

Mechanical
Jul 31, 2018
14
Hi All,
I was looking thru the API standard 661 for Air-cooled Heat Exchangers regarding partition plates and I cannot seem to find a wipe hole. Should there be a wipe hole on the partition plates for the fin fan coolers. Please see attached wipe hole on the partition plate.
 
 https://files.engineering.com/getfile.aspx?folder=f99ff349-8fd1-42f2-85f5-48fe98466a9f&file=DSC_1746.JPG
Replies continue below

Recommended for you

I would assume you mean weep holes or trou holes. They are provided for (horizontal) pass partition plates as drain after hydrotest or, from what I've read here also, to prevent large differential pressures.

Regards,
RaymondN
 
Thanks Raymond for the correction ( weep hole). My concern is we have been experience tube leaks on our Fin fan cooler especially LPG Stabilizer Condenser three pass so our Management decided to plug the outlet tubes as per the attached drawing. My Question is will product leak thru the weep hole and build-up pressure on the other side were the partition is considering it also has a weep hole.

Please see attached drawing

Regards,
Edward Aisa
 
 https://files.engineering.com/getfile.aspx?folder=220a000f-db7b-4dc2-83de-59100230b328&file=E-146_Stabilizer_Condenser.pdf
Dear mafla jones,

Is it not the right time to replace / completely retube the air cooler?

You are not plugging more than 20 percent of the total tubes, are you?

When you are cutting off a partition, why bother about the weep hole? Seal it off with welding or belzona.

Regards.

DHURJATI SEN
 
Raymond, The only problem we now have is we did not seal weld or apply belzona on the weep hole especially on the other side or the left side partition plate as per the attached drawing and the fin fan cooler was given over to operation for start-up.

Regards,
Maflajones
 
 https://files.engineering.com/getfile.aspx?folder=186ad615-c127-454f-98ad-b6eab2374273&file=E-146_Stabilizer_Condenser.pdf
This hole is for vent air during hydrostatic test.

Regards
r6155
 
Raymond, I don't think its a vent hole especially a weep hole inside the Air cooler partition plate because the vent we have on the Finfan cooler is 1/2 pipe located on the header.

Regards,
Mafla jones

 
There is a portion between the top of the pass partition plate and bottom row of tubes that liquid would be stagnant. You need to keep those holes for that portion to drain especially after hydrotest. It wouldn't have much effect on the performance of the air fin cooler. That is also being done for shell-and-tube heat exchanger pass partition plates.

Regards,
RaymondN
 
Please see ASME VIII Div 1 UG-99 (i) Vents shall be provided at all high points of the vessel
in the position in which it is to be tested to purge possible air pockets while the vessel is filling.

Regards
r6155
 