Application Area Definition - Centered btw Sprinklers or not?

Status
Not open for further replies.

UFT12

Mechanical
Mar 16, 2016
311
I would like to post this general question, mainly to the reviewers/regulators visiting this forum.

When you get drawings showing an application area (AA) such as this...

2019-05-18_09_25_56_ufriii.jpg


do you consider it fine? I personally don't as the area limits are not centered between sprinklers. The problem with this, the way I understand it through many drawings I have received, is that many play this trick to skip one or two sprinklers that would normally have to be included in the AA when centered btw sprinklers.

Would you consider it OK or would you reject the design? Any thoughts appreciated.
 
Replies continue below

Recommended for you

I would reject. They need to flow 8 sprinklers on 4 lines and 3 on the last line. That would get them the same 35 sprinklers.

1.2 * DA^0.5. If you exceed the mid spacing between sprinklers with that length, you go to the next sprinkler. That is just basic NFPA 13 as I have always understood it.

Travis Mack, SET, CWBSP, RME-G, CFPS
MFP Design, LLC
 
What that guy said.

It states a MINIMUM of 1.2 times..

So you cannot just draw 37 feet, or whichever the area works out to.

R/
Matt
 