I'm curious how others are dealing with the 2007 NESC arc-flash protection requirements and the apparent contradictions with existing NFPA 70E?
In particular, I'm wondering about the provisions for dealing with systems less than 1000 V. The NESC says that in lieu of doing an actual arc-flash study, a hazard of 4 cal/cm2 can be assumed under 1000 V. For 480 V systems, this can be absurdly low when compared with the requirements of NFPA 70E and IEEE 1584. This is especially true when dealing with the 480V portion of a pad-mounted transformer that probably has minimal primary protection.
Does anyone know the basis or origin of the 4 cal/cm2??
Also, for substations using metal-clad switchgear, the IEEE 1584 calculations would seem to be much more relevant than the NESC tables when dealing with switchgear. Anyone made any decisions on this?
In particular, I'm wondering about the provisions for dealing with systems less than 1000 V. The NESC says that in lieu of doing an actual arc-flash study, a hazard of 4 cal/cm2 can be assumed under 1000 V. For 480 V systems, this can be absurdly low when compared with the requirements of NFPA 70E and IEEE 1584. This is especially true when dealing with the 480V portion of a pad-mounted transformer that probably has minimal primary protection.