Hey guys, a project that I am working on has me questioning some of the traditional beliefs I had regarding the use of electric vs pneumatic valve actuators. Can you guys give me your insight on the following issue.
Our company has been awarded the construction of an energy plant at a large university and I have noticed that the engineer has specificed all control valves (modulating and 2 position) to be pneumatic actuators. The valves with actuators in question are on the chilled and condenser water systems.
My beliefs on when you would use pneumatics vs electric where based on the following assumptions;
PNEUMATICS
- typically used for modulating applications such as compressor recycles, tank/steam drum level control where precise control is required and the valve will be opening and closing often. These are conditions that throughout the life of the valve would stress an electric actuator and in order to move the valve fast enough, electric actuators would take a decent amount of power to perform so air is used to drive a piston, rather than use an electric actuator.
- typically used for 2 position applications where there are concerns of safety dealing with a power outage (such as on a natual gas safety valve, or steam turbine safety valves) where you can have an air accumulator tank and know that there is always are to operate your valve or used where very high closing torques are needed due to closing a valve against a high differential pressure. I can't think of any good examples of the top of my head.
ELECTRIC
- Would typically be used for 2 position valves that are not going to close against very high differential pressures. The higher the DP the larger and more complex the motor/gearset gets (from probalby needing higher torque, the more power you consume, etc...) Also a factor is that the valves are not going to be moving very often, so there is little risk of damaging the motors from overheating.
- Electric actuators can also be used in modulating service, but would not be ideal where very precise control is needed, due to not wanting to have to have an overly large motor size and the constant abuse on the motor. Here I am thinking of small bellimo electric actuators that are often attached to valves. These tend to have very long stroke times.
Can you guys please confirm if my assumptions are correct and if not please correct me where I am wrong. There seems to be a general concensus that at utility plants most actuators are pneumatic, but I think that most actuators at utility plants are meetings the requirements stated above for pneumatic actuators. Where as the electric actuators that are seen in the HVAC world on isolation valves would meet the requirements listed above for electric actuators.
Thanks in advance for any help.
Our company has been awarded the construction of an energy plant at a large university and I have noticed that the engineer has specificed all control valves (modulating and 2 position) to be pneumatic actuators. The valves with actuators in question are on the chilled and condenser water systems.
My beliefs on when you would use pneumatics vs electric where based on the following assumptions;
PNEUMATICS
- typically used for modulating applications such as compressor recycles, tank/steam drum level control where precise control is required and the valve will be opening and closing often. These are conditions that throughout the life of the valve would stress an electric actuator and in order to move the valve fast enough, electric actuators would take a decent amount of power to perform so air is used to drive a piston, rather than use an electric actuator.
- typically used for 2 position applications where there are concerns of safety dealing with a power outage (such as on a natual gas safety valve, or steam turbine safety valves) where you can have an air accumulator tank and know that there is always are to operate your valve or used where very high closing torques are needed due to closing a valve against a high differential pressure. I can't think of any good examples of the top of my head.
ELECTRIC
- Would typically be used for 2 position valves that are not going to close against very high differential pressures. The higher the DP the larger and more complex the motor/gearset gets (from probalby needing higher torque, the more power you consume, etc...) Also a factor is that the valves are not going to be moving very often, so there is little risk of damaging the motors from overheating.
- Electric actuators can also be used in modulating service, but would not be ideal where very precise control is needed, due to not wanting to have to have an overly large motor size and the constant abuse on the motor. Here I am thinking of small bellimo electric actuators that are often attached to valves. These tend to have very long stroke times.
Can you guys please confirm if my assumptions are correct and if not please correct me where I am wrong. There seems to be a general concensus that at utility plants most actuators are pneumatic, but I think that most actuators at utility plants are meetings the requirements stated above for pneumatic actuators. Where as the electric actuators that are seen in the HVAC world on isolation valves would meet the requirements listed above for electric actuators.
Thanks in advance for any help.