ARC FLASH LABELING - NFPA 70E Article 130.5 (D) Equipment Labeling
4
Hello All,
I was curious about NFPA 70E Article 130.5 (D) Equipment Labeling. The article states "Electrical equipment such as switchboards, panelboards, industrial control panels, meter socket enclosures, and motor control centers that are in other than dwelling units and that are likely to require examination, adjustment, servicing, or maintenance while energized shall be field-marked with a label." My question is if you did not account for every "control panel" on the project that was not within your purchase order or clearly labeled on your "scope" of work at the beginning of the project have you violated this code statement? I would think that if a contractor had an energized work permit to work on something live and the equipment (maybe a control panel or remote VFD) did not have a label on it they would not touch it until further consultation. Thank you again for your help.
Best Regards,
Engineer in Training
There is a fallback position in NFPA 70E that allows work in the absence of labels if the work is done in accordance with the task tables included in NFPA 70E.
old field guy
A qualified person could check if there's a label upstream of the equipment to be serviced.