Arc Flash Min and Max Utility Fault Values

Status
Not open for further replies.

pistola2

Petroleum
Jan 31, 2004
3
CA
Hi. I wish to understand more about how the utility contribution to an arc flash calculation is done. Do you require the utility to supply both maximum and minimum fault values to help define the min and max arcing current? If so, which values? 3-phase only or single line to ground (or both)? I think the IEEE standard only talks about 3-phase values. thank you
 
Replies continue below

Recommended for you

Yes, both if you can get it. 3-phase only. Also try searching here for other threads on this topic.

Alan