ScottyUK/UKEng,
I have been predominatly working in the UK/Europe Paper & Pulp Industry over the last 10-15years,but only came into contact with Arc Flash Studies early last year.
The studies I have conducted are based on using SKM Power Tools software - CAPTOR & DAPPER incorporating IEC60909
Fault Analysis
I too would also be delighted to share "lessons learnt".
Here are a few to start off with for comment,based 1st on the short circuit study:
1)Obtain all the scenarios from the Supply Utility re;Ibreak,Ipeak and X/R ratios for the incoming point of supply.Other consumers connected to the same supply(MV) may have embedded generation which can add to the fault level.
Only became apparent when I requested the supply X/R ratio!
2)Obtain a copy of the G74 Engineering Recommendation.The UK Utilities I was obtaining Fault Level info from,refer to this document.It is also very useful e.g.in identifying values of X/R ratios for large synch/asynch machines,if you don't have access to data re; older machines
3)Obtain a copy of the IEC60909-A must.The references and diagrams explaining fault contribution for the near-and-far fault contribution from large generators/motors I found particularly useful.This also helped to understand which parameters to set in SKM when dealing with motor fault contributions re; first 5/6cycles or otherwise
4)I didn't use the SKM power tools default values for transformer X/R ratios based on %Z,calculate from transformer losses etc.The SKM default values can produce inaccurate Ipeak values.
5)Obtain typical UK(50Hz)motor supplier r/x and locked rotor/FLC values-more accurate then SKM default values.
Similarly I checked cable data with a major European cable manufacturer-The SKM cable databse were fine(SWA/XLPE/PVC)
6)The G74 document is very useful as a guideline for x/r value and ratio of locked rotor/rated current if you have large regen/active rectifier static invertors/convertors (600-1500kW in my case),but don't have equipment actual values.I contacted SKM on this topic but felt that their reply was not what I had expected,so used the G74.
Incidentally the short circuit analysis was specifically also used to identify that bus,switchgear ,ACB/MCC's etc were adequately fault rated re:Ibreak and Imake(Ipeak)
The coordination study was also used to identify that discrimination was being met and to see whether improvements could be made.
If this is of any help I will list my other"lessons learnt" on the coordination and Arc Flash studies in due course.Would be interested to share your experience