stevesummers
Electrical
- Nov 2, 2015
- 26
Hi All,
so i am doing an arc flash study to IEEE 1584 using ETAP, and have been working through the various calculations etc.. Most of the answers are fine, but a few results are high and i have various mitigation measures like ZSI and arc flash sensors to consider. I am at early concept stage so we don't have any specific switchegar in mind, and i am also using typical fault clearnace times and switchgear dimensions so i know things are a little imprecise.
But i started to think about the actual switchgear design itself. I know that in addition to the various mitigation measures, we can also specify arc-proof switchgear, which is rated to withstand an arc blast, and direct some/most of the arc energy to a vent duct or similar.
So my question is from a power system studies point of view, does specifying normal or arc-proof switchgear actually make any difference to the study results? I.e. if i am getting 50cal/cm^2 with a generic switchgear would using a similar arc resisitant switchgear actually reduce that incident energy level down to help protect the individual / reduce PPE, or is it more to protect the physical switchgear itself, and doesn't cause any reduction to the energy levels if someone was undertaking mainteance work?
I know there are vairous levels of arc proof design, i was just wondering about the basic concept...
so i am doing an arc flash study to IEEE 1584 using ETAP, and have been working through the various calculations etc.. Most of the answers are fine, but a few results are high and i have various mitigation measures like ZSI and arc flash sensors to consider. I am at early concept stage so we don't have any specific switchegar in mind, and i am also using typical fault clearnace times and switchgear dimensions so i know things are a little imprecise.
But i started to think about the actual switchgear design itself. I know that in addition to the various mitigation measures, we can also specify arc-proof switchgear, which is rated to withstand an arc blast, and direct some/most of the arc energy to a vent duct or similar.
So my question is from a power system studies point of view, does specifying normal or arc-proof switchgear actually make any difference to the study results? I.e. if i am getting 50cal/cm^2 with a generic switchgear would using a similar arc resisitant switchgear actually reduce that incident energy level down to help protect the individual / reduce PPE, or is it more to protect the physical switchgear itself, and doesn't cause any reduction to the energy levels if someone was undertaking mainteance work?
I know there are vairous levels of arc proof design, i was just wondering about the basic concept...