mls1
Electrical
- Aug 15, 2002
- 133
I'm working on a study for a client interested in replacing existing MCCs with arc resistant MCCs. All of the duration rated MCCs I've found have a duration rating of only 100 ms. For this particular system, the available fault current is less than 20 kA. With the short time trip delay on the upstream feeder breaker they do have levels of about 10 cal/cm2. However, to meet the manufacturer arc resistant rating they would have to use an instantaneous trip to keep the arc duration less than 100 ms. At that point they are already at a very low energy level. Common sense says the C37.20.7 rating requires the manufacturer to run the test at MCC rated fault current so the gear would be resistant at lower fault levels for a longer period but there is nothing that documents that. It seems to me that if they have to adjust delay settings or use a device rating to get an arc resistant rating there's really no point in using arc resistant gear. Just lower the energy level and call it good. Am I missing something here?