jmbelectrical
Electrical
- Jul 16, 2011
- 126
I am investigating an incident in which a failure, resulting in a fire, occurred at a 480/277V, three-phase, four-wire panelboard. I do not know the causation of the failure at this time, however, I know that arcing occurred at some point due to the presence of irregularly-shaped openings along the panelboard's enclosure.
The panelboard was supplied by a service disconnect switch, fused at 400A with dual-element time delay fuses. None of the fuses blew. The panelboard was supplied by an insulated, #2 AWG (copper) equipment grounding conductor which originated at the service disconnect switch. The equipment grounding conductor lug located within the service disconnect switch arced off such that a portion of its fastener (that is, the fastener used to attach the lug to the enclosure) was missing. The lug was detached from the disconnect switch's metallic enclosure wall. Evidence of arcing (burn marks and an irregularly-shaped opening) was also observed adjacent to the disconnect switch's neutral conductor lugs.
The electrical utility transformer had a capacity of 150kVA. Based on its %Z, the maximum secondary-side fault current is just over 4,000A, assuming an infinite primary bus.
I know that arcing faults are associated with fault currents 30 to 50 less than that of a bolted three-phase fault, however, I still expected one or several of the fuses to blow at some point during the incident. Is this a reasonable expectation? And what could have caused arcing and detachment of the equipment grounding conductor lug within the service disconnect switch? Is this simply a matter of insufficient fault current for it to be cleared?
The panelboard was supplied by a service disconnect switch, fused at 400A with dual-element time delay fuses. None of the fuses blew. The panelboard was supplied by an insulated, #2 AWG (copper) equipment grounding conductor which originated at the service disconnect switch. The equipment grounding conductor lug located within the service disconnect switch arced off such that a portion of its fastener (that is, the fastener used to attach the lug to the enclosure) was missing. The lug was detached from the disconnect switch's metallic enclosure wall. Evidence of arcing (burn marks and an irregularly-shaped opening) was also observed adjacent to the disconnect switch's neutral conductor lugs.
The electrical utility transformer had a capacity of 150kVA. Based on its %Z, the maximum secondary-side fault current is just over 4,000A, assuming an infinite primary bus.
I know that arcing faults are associated with fault currents 30 to 50 less than that of a bolted three-phase fault, however, I still expected one or several of the fuses to blow at some point during the incident. Is this a reasonable expectation? And what could have caused arcing and detachment of the equipment grounding conductor lug within the service disconnect switch? Is this simply a matter of insufficient fault current for it to be cleared?