Arcing Ground Faults

Status
Not open for further replies.

Gibbs

Electrical
Apr 4, 2000
4
0
0
US
Visit site
I have a 3 phase, 4-wire, 120/240 volt delta service to a machine shop. I have recently had some 3 phase equipemnt damaged: an inverter, transformer, and 2 three phase surge protectors damaged from high voltage. There was no damage to any single phase equipment. I suspect an arcing ground fault. Any information on this subject and references would be appreciated. Also any suggestions on how to locate the point of fault.
 
Replies continue below

Recommended for you

Suggestion: A ground fault transformer with the high-resistance grounded neutral, the ground fault monitoring and possibly trip.
References:
1. D. Beeman "Industrial Power Systems Handbook," McGraw-Hill Book, Co., 1955
2. ANSI/IEEE Std 242-1986 Chapter 7 "Ground Fault Protection"
 