Even in "ungrounded" systems, there is an unavoidable capacitive coupling between the phase conductors and ground. When there is an intermittent fault, the unfaulted phases initially have phase to ground voltage equal to the normal phase voltage (e.g. 480 V). If the arcing fault stops, this voltage discharges through the capacitive coupling to ground based on the X/R time constant. But if another arc occurs before the voltage goes fully down, the voltage can increase to much greater than normal phase voltage. Similar to voltage doubler circuits in electronics. This can be quite nasty for motor windings.
If you search for "repetitive restrike" you'll find more information and a much better explanation than I've given you.