Are drains required in all rigid metal conduits per the NEC?

Status
Not open for further replies.

bdn2004

Electrical
Jan 27, 2007
799
NEC article 225.22 seems to indicate that drains are required in outdoor conduits. If so, I wonder why this requirement is not in Section 344.
 
Replies continue below

Recommended for you

The rule in 225 is a more general rule and applies to all raceways run outside. What I don't find is a rule that requires a drain for raceways that are run in interior wet locations.
There is a specific rule in 230.53 for service raceways and a rule in 368.23 for busways.
 
Regardless of rules, you need a drain anywhere condensation might form.

Good on ya,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies
 
Oops, sorry -- I posted too quick.

If no condensation expected, no drain required. So not all rigid needs one.

Good on ya,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies
 