A proposed structure is inside fence of a refinery. Does state officials have authority to enforce the structure comply with IBC code?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
dauwerda said:Typically this question arises with non-structural requirements that are in the IBC. Such as, the IBC essentially requires that all (non-residential) stairs have a max rise of 7" and a min run of 11", OSHA allows up to a 10" rise and a 10" run. In industrial facilities, this can be a huge difference in the cost and size of a structure as it takes a much larger footprint to fit the "IBC compliant" stairs (typically, its the footprint that is the issue). I don't see wanting to follow OSHA requirements but not IBC requirements as a lack of ethics in this case.
Great! I wish more AHJ's took this stance, but this is an example of one local AHJ out of how many in the US? Did this AHJ even have an adopted building code? Many of the industrial facilities I have worked in are in areas that don't have an enforceable (i.e. not adopted into law) building code and therefore never have any issues like this either.retired13 said:I worked in a large industrial plant (like a small town) for 5 yeas, all designs were abided with the owner's specification, and was never required to go to the local jurisdiction.
Just because there was no involvement/interference and nothing happened doesn't mean that's how it should have been handled. Many people speed and never get a traffic ticket, that doesn't mean they are in compliance with the law.retired13 said:I even witnessed the plant operation engineer took out an old bridge and rebuilt without interference from the local, and/or the DOT, thought the bridge was on a public road in the private land.
I have worked on substations and power plants that did have to submit everything to the AHJ and I have worked on them where they didn't. The entire point I have been trying to make here is that it depends on the location of the facility and the AHJ and what they have or haven't adopted into law.retired13 said:I also worked on nuclear power plant, hydroelectric powerplants, and some electrical substations, I wonder how much weight IBC, or any building code, has on these industries, or the mind of those authorities.
The following I read as code exempt:
(a)Building and structures specifically regulated and preempted by the Federal Government.
(b)Railroads and ancillary facilities associated with the railroad.
(c)Non-residential farm buildings on farms.
(d)Temporary buildings or sheds used exclusively for construction purposes.
(e)Mobile homes or modular structures used as temporary offices, except that the provisions of part V (§§ 553.501—553.513, Florida Statutes) relating to accessibility by persons with disabilities and permits shall be required for structural support and tie down, electric supply and all other such utility connections to such mobile or modular structures as required by this jurisdiction.
(f)Those structures or facilities of electric utilities, as defined in § 366.02, Florida Statutes, which are directly involved in the generation, transmission, or distribution of electricity.
(g)Temporary sets, assemblies, or structures used in commercial motion picture or television production, or any sound-recording equipment used in such production, on or off the premises.
(h)Chickees constructed by the Miccosukee Tribe of Indians or the Seminole Tribe of Florida. As used in this paragraph, the term "chickee" means an open-sided wooden hut that has a thatched roof of palm or palmetto or other traditional materials, and that does not incorporate any electrical, plumbing, or other non-wood features.
(i)Family mausoleums not exceeding 250 square feet in area which are prefabricated and assembled on site or preassembled and delivered on site and have walls, roofs, and a floor constructed of granite, marble, or reinforced concrete.
(j)Temporary housing provided by the Department of Corrections to any prisoner in the state correctional system.
(k)Building or structure having less than 1,000 square feet, which is constructed and owned by a natural person for hunting, and which is repaired or reconstructed to the same dimension and condition as existed on January 1, 2011, if the building structure1)is not rented, leased, or used as a principal residence; and(2)is not located within the 100-year floodplain, according to the Federal Emergency Management Agency's current Flood Insurance Rate Map; and(3)is not connected to an offsite electric power or water supply.
102.2.1 In addition to the requirements of §§ 553.79 and 553.80 Florida Statutes, facilities subject to the provisions of Chapter 395 Florida Statutes and Part II of Chapter 400 Florida Statutes shall have facility plans reviewed and construction surveyed by the state agency authorized to do so...(basically hospitals I think)
102.2.2 Residential Buildings or structures moved into or within Hernando County shall not be required to be brought into compliance with the state minimum building code....
102.2.4 This section does not apply to the jurisdiction and authority of the Department of Agriculture and Consumer Services to inspect amusement rides or the Department of Financial Services to inspect state-owned buildings and boilers.
102.2.6 This section does not apply to swings and other playground equipment accessory to a one- or two-family dwelling.
Following I read as permit exempt but not code exempt:
105.2 Work exempt from permit. Exemptions from permit requirements of this code shall not be deemed to grant authorization for any work to be done in any manner in violation of the provisions of this code. Permits shall not be required for the following:
Building:
1.One-story detached accessory structures used as tool and storage sheds, playhouses and similar uses, to a Group R-3 occupancy provided the floor area does not exceed 120 square feet, at grade level.
2.Oil derricks.
3.Water tanks supported directly on grade if the capacity does not exceed 5,000 gallons (18 925 L) and the ratio of height to diameter or width does not exceed 2:1.
4.Sidewalks and driveways not more than 30 inches (762 mm) above adjacent grade, and not over any basement or story below and are not part of an accessible route.
5.Painting, papering, tiling, carpeting, cabinets, counter tops and similar finish work.
6.Temporary motion picture, television and theater stage sets and scenery.
7.Prefabricated swimming pools accessory to a Group R-3 occupancy that are less than 24 inches (610 mm) deep, do not exceed 5,000 gallons (18 925 L) and are installed entirely above ground.8.Shade cloth structures constructed for nursery or agricultural purposes, not including service systems.
...
Following I read as exempt from plan review but not the code:
107.3 Examination of documents. The building official shall as deemed necessary examine or cause to be examined each application for a permit and the accompanying documents, consisting of drawings, specifications, computations and additional data, and shall ascertain by such examinations whether the construction indicated and described is in accordance with the requirements of the technical codes and all other pertinent laws or ordinances.
Exceptions:
1.Building plans approved pursuant to § 553.77(5) Florida Statutes and state-approved manufactured buildings are exempt from local codes enforcing agency plan reviews except for provisions of the code relating to erection, assembly or construction at the site. Erection, assembly and construction at the site are subject to local permitting and inspections. Photocopies of plans approved according to F.A.C. 9B-1.009, F.A.C. shall be sufficient for local permit application documents of record for the modular building portion of the permitted project.
2.Industrial construction on sites where design, construction and fire safety are supervised by appropriate design and inspection professionals and which contain adequate in-house fire departments and rescue squads is exempt, subject to local government option, from review of plans and inspections, providing owners certify that applicable codes and standards have been met and supply appropriate approved drawings to local building and fire-safety inspectors.