Hi all,
working on a project with a client
I know NFP 497 says generally the area classification is usually a 15' radius from a natural gas vessel/ valve etc.
I did some digging and it said to determine the actual distance instead of using the 15' rule to refer to API 505
API 505 further refers to IEC 60079-10-1 to calculate the extent of the classification area.
Is this the correct way to approach this? I took a look at IEC 60079-10-1 and it does give a good methodology and determining the zone.
for those wondering, client asked me to do this since their space is a bit tight. they want to know if we can get the hazard zone less then 15'