I have a situation in which the substation source (12.47 kV, L-L, grounded-wye) is feeding a 500 KVA, 3-phase padmounted distribution transformer (delta-connected primary windings).
There are surge arresters connected phase-ground at the phase connections on the primary side of the padmounted transformer. The current surge arrester ratings are 9 kV
(> 7.2 kV L-G source voltage).
When the transformer is first energized, it is done so one phase at a time.
When the last and final phase is energized, the surge arrester "blows".
My hunch is the transformer inrush current causes a phase imbalance, resulting in a phase-phase overvoltage at the primary terminals of the padmounted transformer, exceeding the 9 kV phase-ground arrester rating.
Should I be increasing the arrester rating to 12 kV?