Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations GregLocock on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

AS1657 and safety factors

Status
Not open for further replies.

Xtli

Structural
Aug 13, 2014
2
Hi gentlemen,

AS1657 refers to AS1170 standards. In AS1657 there is design load of 550 N or 600 N for hand rails. Is this the design value to be used in calculation or should this be multiplied by safety factor 1.5?

-Xtli
 
Replies continue below

Recommended for you

They are treated as a live load, so multiplied by a load factor of 1.5 for ULS. No load factor for SHS.
 
Thank you.

Can you also tell me which part of the srandard tells this?
I would like to learn to read these AS standards.
 
It's classified as an imposed action in 1170.1 (i.e. Q = live load) , load factor for imposed actions in 1170.0 is 1.5.

SHS should have read SLS in my previous reply.
 
Status
Not open for further replies.

Part and Inventory Search