Hey everybody,
I refer you to table 5.6.4 note 1: "The first order eccentricity"... blah blah... "e/b has been taken as <=0.025 with emax = 100mm". I take it this clause limits the table usage to columns with tiny moments and high axial loads.
For example I'm designing a 600 by 300 column which is 4000mm high. I'm taking the effective length as 4m because only the 300mm wide face is attached to the slab, thus I can't use table 5.6.3 as it is limited to columns with an eff. length less then 3m. My fire actions are 380kN and 195kNm respectively which give an e=513mm! Which means that I can't use table 5.6.4 either cause e must be less then 100mm. Apart from using the Eurocode 2, referenced in clause 5.3.1, how else do I get a fire-rating for this column?
I think this eccentricity limit is a little over the top and should be reviewed, anyone else care to comment?
I refer you to table 5.6.4 note 1: "The first order eccentricity"... blah blah... "e/b has been taken as <=0.025 with emax = 100mm". I take it this clause limits the table usage to columns with tiny moments and high axial loads.
For example I'm designing a 600 by 300 column which is 4000mm high. I'm taking the effective length as 4m because only the 300mm wide face is attached to the slab, thus I can't use table 5.6.3 as it is limited to columns with an eff. length less then 3m. My fire actions are 380kN and 195kNm respectively which give an e=513mm! Which means that I can't use table 5.6.4 either cause e must be less then 100mm. Apart from using the Eurocode 2, referenced in clause 5.3.1, how else do I get a fire-rating for this column?
I think this eccentricity limit is a little over the top and should be reviewed, anyone else care to comment?