ChipB
- Apr 21, 2001
- 347
Hey all:
I've been away from the threads for a while. Sorry...
I'm evaluating a building using this standard. In Chapter 7 of ASCE 41-13, it defines the Gravity Loads, Qg as 1.1(Dl+0.25LL+SL). It does get a little bit further in defining what to use for torsional effects, etc, however, it really doesn’t discuss the use in evaluation that I can see. It doesn’t define a method (ASD or LRFD).
The way I am interpreting it is:
The 1.1QD+L+S Value is to be used in place of D in 1.2D + 1.0E + L + 0.2S of the Strength Design Formula
Effectively creating the formula: 1.2(1.1QD+L+S) + 1.0E + L + 0.2S
Which once you go to Chapter 12 of ASCE 7-10 creates the formula:
(1.2+0.2Sds)(1.1QD+L+S ) + 1.0E + L + 0.2S
And
The 0.9QD+L+S Value is to be used in place of D in 0.9D + 1.0E
Effectively creating the formula: 0.9(0.9QD+L+S) + 1.0E
(0.9-0.2Sds)(0.9QD+L+S) + 1.0E
Am I interpreting this correctly? ASCE 41-13 specifically states, it is a “Standard”. So do I take this “Standard” and evaluate the building using the load combinations above?
To be honest, I will be using ASD combinations, not strength, but the same principle applies.
Thanks in advance,
Chip
And
Thanks in advance,
Chip