OC_eit
Structural
- Apr 23, 2018
- 2
Hi all,
I recently got a comment from a plan checker that I must use 4 PSF minimum for the dead load of any ceilings on my project, irregardless of the actual ceiling weight, for both gravity and lateral design. He cites ASCE 7-10, Section 13.5.6.1, specifically where it mentions that "W[sub]p[/sub] shall not be taken as not less than 4 psf...". My issue with his comment is that I, as well as other engineers in my office, interpret this 4 psf minimum as only applying to the F[sub]p[/sub] force one would use to design the bracing and anchorage of the ceiling, not to the load we use for the overall gravity and lateral design of the building. So my question to you all is what would be the most correct interpretation of this code section?
Thanks for the help.
I recently got a comment from a plan checker that I must use 4 PSF minimum for the dead load of any ceilings on my project, irregardless of the actual ceiling weight, for both gravity and lateral design. He cites ASCE 7-10, Section 13.5.6.1, specifically where it mentions that "W[sub]p[/sub] shall not be taken as not less than 4 psf...". My issue with his comment is that I, as well as other engineers in my office, interpret this 4 psf minimum as only applying to the F[sub]p[/sub] force one would use to design the bracing and anchorage of the ceiling, not to the load we use for the overall gravity and lateral design of the building. So my question to you all is what would be the most correct interpretation of this code section?