ASCE -7-10 components and cladding wind corner zones 4

Status
Not open for further replies.

panelguy1

Structural
Jan 10, 2018
4
I'm currently working on a project where one of the "corner" is 130°. I have searched everywhere in ASCE 7-10 to find out what the maximum angle can be for a wall zone to be considered a corner. Will I have to consider this area as a corner zone?
 
Replies continue below

Recommended for you

I haven't seen anything in the code about this but I'd go with engineering judgment on this one and say it's not a corner.
 
I'd go the other way - any semblance of a corner will create interruptions in the laminar wind flow and cause higher stresses.
For 130 degree...perhaps not as much as a 90 degree....but you don't have anything else to go on except being conservative or paying for a wind tunnel test.



Check out Eng-Tips Forum's Policies here:
faq731-376
 
170° or less is a corner zone.

Background information can be found in "SEAW/ATC-60 Commentary on Wind Code Provisions"
or
Slide 72
 
Check the commentary of ASCE 7-16. There is information regarding corners of that nature. That indicates an included interior angle greater than 135 need not be considered as a corner. So your 130 degrees would just qualify as a corner.
 