Deadblow
Structural
- Jul 13, 2015
- 140
Hello,
I am working on the foundation designs for a pre-engineered metal building that was designed according to the 2015 IBC and ASCE 7-10. This is my first foundation design using the 2015 IBC and the "new" wind loads. I am accustom to the 2009 IBC. I feel like this topic has been beat to death, but I still don't understand which load combination set, strength design (ASCE 7-10 2.3) or allowable stress design (ASCE 7-10 2.4), I should be using throughout my foundation design. The PEMB manufacturer has provided all of the reactions that come out of the column base plates. These reactions are noted to be "un-factored". The wind load reactions are at a "strength" value with a load factor of 1.0.
My design to check soil bearing pressures. I always believed that I check the service level applied soil bearing against the "allowable" soil bearing pressure. I think I should use the load combinations found in the allowable stress design (ASCE 7-10 2.4) to check this. For me, the governing load combination is "D+S" which results in bearing pressure of (11.7kips + 18.0kips)/36sq.ft = 0.825ksf < 2.0ksf therefore ok. Anybody disagree with this?
My design to check uplift on the footing. Per the notes from the PEMB manufacturer, I figured I should be using the load combinations found in the strength design (ASCE 7-10 2.3). For me, the governing load combination is "0.9D+1.0W" which results in uplift of (0.9x11.7kips + -13.5kips) = -2.97kips. Therefore my footing, and soil overburden need to weigh at least (2.97kip/0.9) = 3.3kips. Anybody disagree with this?
What if I use the allowable stress design load combinations to check the uplift on the footing? For me, the governing load combination is "0.6D+0.6W" which results in uplift of (0.6x11.7kips + 0.6(-13.5kips)) = -1.08kips. Therefore my footing, and soil overburden need to weigh at least (1.08kip/0.6) = 1.8kips. So which is it, 3.3kips or 1.8kips, and why? I used to just check uplift using "0.6D+W" per the allowable stress design load combinations of the 2009 IBC. For what it's worth, the software program that I use to double check my foundation designs is using "0.6D+0.6W", which is an allowable stress load combination, for both the soil bearing check and the uplift check. I don't understand why I end up with two different required footing sizes.
Which set of load combinations should I use for the design of the anchor bolts, ASD or LRFD?
The design of the concrete and reinforcement in the footing needs to be designed for the LRFD load combination, correct? It seems to me there is a lot of mixing load combination sets occurring. Is this correct?
Thanks for any explanations!
EIT
I am working on the foundation designs for a pre-engineered metal building that was designed according to the 2015 IBC and ASCE 7-10. This is my first foundation design using the 2015 IBC and the "new" wind loads. I am accustom to the 2009 IBC. I feel like this topic has been beat to death, but I still don't understand which load combination set, strength design (ASCE 7-10 2.3) or allowable stress design (ASCE 7-10 2.4), I should be using throughout my foundation design. The PEMB manufacturer has provided all of the reactions that come out of the column base plates. These reactions are noted to be "un-factored". The wind load reactions are at a "strength" value with a load factor of 1.0.
My design to check soil bearing pressures. I always believed that I check the service level applied soil bearing against the "allowable" soil bearing pressure. I think I should use the load combinations found in the allowable stress design (ASCE 7-10 2.4) to check this. For me, the governing load combination is "D+S" which results in bearing pressure of (11.7kips + 18.0kips)/36sq.ft = 0.825ksf < 2.0ksf therefore ok. Anybody disagree with this?
My design to check uplift on the footing. Per the notes from the PEMB manufacturer, I figured I should be using the load combinations found in the strength design (ASCE 7-10 2.3). For me, the governing load combination is "0.9D+1.0W" which results in uplift of (0.9x11.7kips + -13.5kips) = -2.97kips. Therefore my footing, and soil overburden need to weigh at least (2.97kip/0.9) = 3.3kips. Anybody disagree with this?
What if I use the allowable stress design load combinations to check the uplift on the footing? For me, the governing load combination is "0.6D+0.6W" which results in uplift of (0.6x11.7kips + 0.6(-13.5kips)) = -1.08kips. Therefore my footing, and soil overburden need to weigh at least (1.08kip/0.6) = 1.8kips. So which is it, 3.3kips or 1.8kips, and why? I used to just check uplift using "0.6D+W" per the allowable stress design load combinations of the 2009 IBC. For what it's worth, the software program that I use to double check my foundation designs is using "0.6D+0.6W", which is an allowable stress load combination, for both the soil bearing check and the uplift check. I don't understand why I end up with two different required footing sizes.
Which set of load combinations should I use for the design of the anchor bolts, ASD or LRFD?
The design of the concrete and reinforcement in the footing needs to be designed for the LRFD load combination, correct? It seems to me there is a lot of mixing load combination sets occurring. Is this correct?
Thanks for any explanations!
EIT