rlmhawk
Structural
- Jun 19, 2012
- 6
Wind loading on walls/signs in Case A of Table 29.4-1 represents a uniform wind load pattern placed on the structure with its resultant acting at the centerline of the fence/wall. Wind loading in Case C represents an oblique loading scenario applied as a stepped load pattern along the wall/sign length based upon length/height ratios. Both of these cases are pretty well defined as far as their application to these structures is concerned. However, load Case B is somewhere in between the two, representing an oblique loading scenario with its resultant acting at 20% off the centerline of the wall/sign. To me, it is not clearly defined as to how you are to apply the load along the full length of the structure as the others are and thus is rather subjective. Such load application is similar to applying a triangular load (in plan) to the wall/sign, where the resultant would be located at 1/3 of the length of wall from the windward end (approximately 7/10 of the wall). However that doesn't seem realistic for a wall wind load scenario given one end gets no load and the other a very high psf load. It seems there could be a wide range of load distribution interpretations that might place the overall resultant at this off center location. To me, a distribution that applies a minimum load to all the wall seems more appropriate than something resembling a triangular approach, most likely one that also uses an alternate stepped approach for example. How have you interpreted the application of wind in load Case B?